11/28/2014 8:18 AM | |
Posts: 3 Rating:
|
Good morning, are there any problems if I use (for example) a 25kVAR contactor (3RT16271AP01) on a 10kVAR capacitor? Thanks |
11/29/2014 10:35 AM | |
Joined: 1/21/2013 Last visit: 11/20/2024 Posts: 4620 Rating:
|
Hello Gabrielez, Please have a look under --> Operational reactive power / at AC-6b Product information - Siemens Industry Online Support With this contactor at 400V minimum is 6 Kvar |
12/1/2014 7:40 AM | |
Posts: 3 Rating:
|
I didn't know there were these technical specifications. Thank you very much! |