Sorry ,I'm new to the PLC World I want to Know which cable connecting the SITRANS Probe LU with SIMATIC S7-300 if possible Full Manual and Image of the cable |
11/10/2010 11:29 PM | |
Joined: 7/2/2008 Last visit: 9/30/2024 Posts: 928 Rating: (309) |
Hello Emad, Welcome to Siemens world. First, the Probe LU has 2 variants, one that is PROFIBUS PA and the other variant is 4 to 20mA with HART communication. Here are the manuals of both variants. SITRANS Probe LU (PROFIBUS PA) - Instruction Manual SITRANS Probe LU (HART) - Instruction Manual In both manuals you will find wiring chapter at page 14. I guess you have the 4 to 20mA (HART) one (If you have the PA Probe LU then it's another story). in page 14 you will read, Notes: . Use shielded, twisted pair cable (wire gauge AWG 22 to AWG 14/ 0.34 mm2 to 2.08 mm2).
|
11/11/2010 6:41 PM | |
Posts: 7 Rating: (0) |
Thanks alot Mr/ H-H for paying attention. Emad Saber |