Hello Amit, to you questions: 1) It is possible to check the functionalyty of the Siwarex FTC without load cells. You can set the Siwarex FTC in simulation mode. With this you can simulate a weight value from PLC or Siwatool. To set the simulation mode active you have to set in Data record 7 S7-Interface/Source for weight simulation to "Weight simulation value of SIMATC/RS232". See also the manual http://support.automation.siemens.com/WW/view/en/26043227chapter 6.13 parmeter SIM_VAL. 2) You can use the full function of the Siwarex FTC also with Siwatool, for the simulation see 1) 3) The Siwarex FTC has 7DI, 8DO and one AO on board. The can only be used for weighing functions. A. The FTC has no input for encoders B. You can use the onboard AO to control the inverter of the feeder. C. The actual feed rate will be calculated by the Siwarex FTC, the feed rate will be only calculated with the weight signal. If it is not possible it will cakculate a substitute value. The flow rate you can see in the PLC and in Siwatool. For more infomation see the manual and the QuickGuide http://support.automation.siemens.com/WW/view/en/39205990. For special questions you can also contact the Siwarex Support hotline.siwarex@siemens.com. Regards ABenno |