6/13/2015 4:06 PM | |
Posts: 13 Rating:
and this image from touch screen |
6/14/2015 12:03 AM | |
Joined: 11/29/2011 Last visit: 8/24/2023 Posts: 1347 Rating:
Hi, The way I see it from here your unit Paramter Protection is ON. See this manual SIWAREX MS - Weigh module for SIMATIC S7-200 under chapter "7.7 Messages via LEDs " It seems like the 5th LED is ON the picture you attached. |
- What you read here, please check with manuals and your requirements. |
6/14/2015 11:20 PM | |
Posts: 13 Rating:
but how to solve it |
6/15/2015 12:36 AM | |
Hi, In the manual SIWAREX MS - Weigh module for SIMATIC S7-200 , chapter "5.2 DS3 Adjustment Parameter": The adjustment data of the DS3 can be protected against rewriting/changing after commissioning with a wire bridge on terminal P-PR (parameter-protection). So check the terminals. Please let us known if the issue is solved or not! |
6/16/2015 9:59 PM | |
Posts: 13 Rating:
sir i have checked all terminals of plc and siwarex ms module and all right the proplem not in the wires or terminals the led of Protection is red because the plc module read high signal from load cell higher than the positive zeroing rang % so now i can't zero this number see in pdf page (11) how to zero this number or rest the siwarex ms module ?
Attachment0900766b80f0dd86.pdf (85 Downloads) |
6/16/2015 11:23 PM | |
Hi, The only thing I found is Parameter Protection SIWAREX MS - Weigh module for SIMATIC S7-200 again in page 5-22 you can read: Send the DS3 to the scale (Not possible with the wire bridge on terminal P-PR, the data is not accepted) Anyhow I understand that this not the answer you are looking for. Please contact your local Siemens Support and let us known what was their recommendation! |