Hi Wino, To Make the Zero the Scale your Can do it from the S7 Progarm also, if the Related Logic is available in the PLC, or you can used the Siwatool via RS232 cable, Here is the Link for the Siwatool Demo Software (But I was never try with Demo Software). & here is the Step How to Do the SIWAREX U calibraation & Which tool you required. in Siwatool you will Find the how to Zero the Scale, & can you tell me one thing it is running Privously Without problem, after what instance you have to required to Zero the weight Scale & the Weighing is Distrube by some one? is in the Tank is fully empty? |
Ammy |
|
4/16/2010 3:11 PM | |
Joined: 1/4/2007 Last visit: 12/5/2024 Posts: 1153 Rating: (175)
|
Hello Wino, You are right: You can zero the sensors only with Siwatool U, if the tank is empty and you don’t need to change the S7 programming blocks. If you want to do later a calibration, I recommend to you the following Quick Guide: http://support.automation.siemens.com/WW/view/en/37733600 |