8/17/2013 8:38 AM | |
Joined: 4/14/2010 Last visit: 11/11/2024 Posts: 525 Rating: (11) |
Dear Sir, Could you describe is the 7MH4950-2AA01 compatible with 7MH5106-3GD00..??? We have selected following items against our appliaction are these items compatible with each other or any thing else please advice. please see attached some detail we will install the load cell with mounting kit at below side of roller conveyor. we have two platform for 1.2 MCB (Meter Cube Box) having weight 200---500kg. kindly advice which one load cell is suitable and compatible with SIWAREX U for this application. bending beam, share beam or Compression type, is this system supported for in motion weighing roller conveyor...?? We wish to install 4 load cell on each roller conveyor.. 7MH4950-2AA01 = 01nos. SIWAREX U WEIGHING ELECTRONICS (TWO-CHANNEL VERSION) * FOR CONNNECTING TWO SCALES * FOR SIMATIC S7-300 AND ET200M * RS232 INTERFACE FOR CONNECT. OF A PC * TTY INTERFACE FOR REMOTE DISPLAY CONNECTION WITH BUS CONNECTOR 6ES7392-1AJ00-0AA0 = 01nos. SIMATIC S7-300, FRONT CONNECTOR FOR SIGNAL MODULES WITH SCREW CONTACTS, 20-PIN 7MH4950-1AK01 = 01nos. CONFIGURATION PACKAGE SIWAREX U FOR SIMATIC S7 IN D/E (CD-ROM) - HSP FOR S7 INTEGRATION - FROM SIMATIC S7 VERSION 5.4 - PC PARAM. SOFTWARE SIWATOOL - MANUAL (CD-ROM) G/E - GETTING STARTED FOR SIMATIC S7 7MH4607-8CA = 01nos. SIWAREX U CONNECTING CABLE 9-PIN -FOR SERIAL LINKING OF SIWAREX U W.9-PIN PC NTERFACE (RS232C) - CABLE LENGTH 3 M 7MH4702-8AG = 50meter LI2Y 2X0,75ST + 2 (2X0,34ST) - CY, SHEATH ORANGE, SPECIAL CABLE FOR CONNECTION SIWAREX MODULE TO JB JUNCTION BOX AND DISTRIBUTION BOX OR IB INTER- MEDIATE BOX AS WELL AS BETWEEN TWO IB"S FOR PERMANENT ON-SITE INSTALLATION;OCCASIONAL BENDING POSSIBLE. 10.8 MM OUTER DIAMETER AMBIENT TEMPERATURE -40 TO +80 CEL. CABLE CUT TO LENGTH, WITHOUT CONNECTOR 7MH4710-1BA = 02nos JUNCTION BOX SIWAREX JB DIE-CAST ALUMINIUM QUALITY TO CONNECT IN PARALLEL UP TO 4 LOAD CELLS IN 4-WIRE OR 6-WIRE SYSTEM DEGREE OF PROTECTION: IP 66 USABLE IN EXPLOSION CAPABLE ATMOSPHERES. IN INTRINSICALLY SAFE ELECTRICAL CIRCUITS DIMENSIONS IN MM:220 X 120 X 81 7MH5106-3GD00 = 08nos. SIWAREX WL 230 LOAD CELL BB-S SA 200KG C3 - RATED LOAD 200KG - ACCURACY CLASS C3 - 3M CABLE LENGTH, 4 CONDUCTOR - MATERIAL STAINLESS STEEL - DEGREE OF PROTECTION IP68 7MH4133-3DC11 = 08nos. SIWAREX R COMBINATION MOUNTING UNIT FOR SERIES BB LOAD CELLS WITH GUARD AGAINST LIFT-OFF AND OSCILLATION LIMIT, CONSISTING OF TOP AND BASE PLATE, FORCE GUIDING PIECE, ELEMENT FOR APPLIC.OF THE FORCE SELF-ALIGNING BOLTS, - MADE OF STAINLESS STEEL, - RATED LOAD 10-200KG 7MH3701-1AA1 = 08nos. GROUNDING CABLE, 400 MM LONG Could you send us price for above items..?? Thanks. AttachmentMCB filling Unit..pdf (565 Downloads) |
MS |
|
8/19/2013 2:07 PM | |
Joined: 1/4/2007 Last visit: 12/13/2024 Posts: 1160 Rating: (175)
|
Hello Sarfraz Bhatti, Yes, the 7MH4950-2AA01 is compatible with 7MH5106-3GD00. Please contact the following person for a quotation: umair.maqsood@siemens.com Best regards Siwarexi |
8/26/2013 11:17 AM | |
Joined: 1/4/2007 Last visit: 12/13/2024 Posts: 1160 Rating: (175)
|
Hello Sarfraz Bhatti, I don’t recommend you to use only 1 load cell for 1 conveyor. If you use only one load cell then you will receive a lower accuracy of the scale. Yes, I mean something like: https://eb.automation.siemens.com/mall/en/WW/Catalog/Products/10024214 You have to create such a mechanics by your own. There exist no MLFB from Siemens. You have to use an oscillation limiter even when you have an intermittent system. Best regards Siwarexi |
11/12/2013 9:00 AM | |
Joined: 4/24/2009 Last visit: 8/20/2024 Posts: 2682 Rating: (135) |
New question splitted to insert FB45 SIWA_U in TIA 12 Best regards O_Moderator |
11/30/2013 1:12 PM | |
Joined: 4/14/2010 Last visit: 11/11/2024 Posts: 525 Rating: (11) |
Dear Siwarexi, please see attached wiring connection and confirm which one usefull diagram for 7MH5103-3PD00..?? i have applied both connection but 7MH4950-2AA01 SF indication is red. following operational error display in SIWATOOL 2 U. Minimum voltage at the sense line undershot. i have checked the following reasons are possible: - The voltage drop in the line up to the junction box (not using junction box) - Line break (it seem ok) - Jumpers missing for 4-wire option (not applied on 6 wire load cell) - Short circuit in the lines. (not found) Thanks. AttachmentDesktop.zip (538 Downloads) |
MS |
|
12/2/2013 10:30 AM | |
Joined: 1/4/2007 Last visit: 12/13/2024 Posts: 1160 Rating: (175)
|
Hello Sarfraz Bhatti, The load cell 7MH5103-3PD00 has a 6-wire connection. You can see the reason for the red LED into the Siwatool software. Send to me your Siwatool file. Afterwards I can take a look into it. Attached you can see how to create a Siwatool file. Best regards Siwarexi AttachmentD:\create_a_SIWATOOL-file.pdf (640 Downloads) |
12/2/2013 1:02 PM | |
Joined: 4/24/2009 Last visit: 8/20/2024 Posts: 2682 Rating: (135) |
New question splitted to measurment value in kg Best regards O_Moderator |