7/9/2014 2:16 PM | ||||||
Joined: 3/17/2014 Last visit: 7/25/2024 Posts: 1 Rating: (0) |
Attachmentfiltecno2_192_168_0_21.zip (150 Downloads) |
|||||
7/9/2014 5:19 PM | |
Posts: 206 Rating: (22) |
Hi Sherkhan, if you have a vibrating chute for dosing you have to be very careful with the EMC. Have a look to chapter 5 of the manual there are some useful hints. http://support.automation.siemens.com/WW/view/en/90229056 If you are sure that EMC is OK. It might be a problem of vibration. There you can use the digital filter. In your attached Siwatool file you have set the low pass filter to 10Hz, This is quite fast you should try to reduce the frequency step by step and look after each step if it is better and if the signal is responding still fast enough. Regards ABenno |