Hi Alex##, if you use the "Ready for use" project from here: http://support.automation.siemens.com/WW/view/en/66825585 Choose the project "MBus_WP231_NAWI_TP700_V209_DE_ENG_FR_TIAV12" If you go to the picture "1.2.4_Quick_Start_Manual_Calibration_1" you can see how to input the calibration weight 1. If you look into the "Press" event of the button with the right arrow, you can see how to transfer the data record 3 (with the calibartion weight 1 inside). I don't know why you got the error message 5001, because the command 2003 is a valid command to read the data record 3 into the buffer of the modbus interface. May be you can send the project, to se how you did it. By the way, basic panels are not allowed to be used with modbus communication and WP231. You should use a comfort panel. Regards ABenno |
8/22/2013 8:10 AM | |
Posts: 3 Rating:
|
Hello again! Thank you for the post. I wanted to confugure the SIWAREX from the PLC not from the panel. I will try to do it like in the example. |
8/26/2013 1:19 PM | |
Posts: 3 Rating:
|
Thank you for your help! |
10/8/2013 5:10 PM | |
Posts: 206 Rating:
|
Hi Sliwka, I can imagine that someone can convert the example project of the WP231 to a basic panel, so that you can open it with TIA-Portal Basic. You should address to the Siwarex Support. Please open a support request here: http://support.automation.siemens.com/WW/view/en/38716036 Regards ABenno |