Hello A_1986, Normally the S7-program for the WP521 is used. You can this S7-proramm on the internet: https://support.industry.siemens.com/cs/ww/en/view/109736579 Here you can find the FB1552. This FB handles the communication between the PLC and the WP521 module. Into the Instance-DB of the FB1552 you can find the status of the load cell at: Static -> s_IO_DATA -> SCALE_STATUS -> “CHANNEL_DISTURBED” If you don’t want to use this FB, you have to disconnect/connect the load cell and try to find out the bit of the load cell by yourself. Best regards Siwarexi |