10/11/2010 7:59 AM | |
Joined: 10/7/2005 Last visit: 3/20/2025 Posts: 3042 Rating:
|
Hello gre_m to start with, cgarcia's K-Bus related conclusion is NOT really applicable to you (a 400 has a "real" K-Bus which is used for user data, a 300 uses the P-Bus as advised HERE). I do however agree with cgarcia's recommendation to use Ob1 for the call of comms blocks to speed things up (assuming OB1's scan time is faster than your OB35 related call rate of 20ms). Having said that, based on Appendix 2 of the CP 341 Point-to-Point Communication, Installation and Parameter Assignment manual you can expect that it'll take 26ms for the transmission of one 50 Byte long message@ 57600baud. I hope this helps |
Cheers |
|
10/12/2010 5:29 PM | |
Posts: 947 Rating:
|
Thank you! tell me, please- where I can read these details? I think that 14 bytes - this is not enough. For 2-cycle I've read 51 bytes. |