2/1/2014 4:43 PM | |
Joined: 8/19/2012 Last visit: 1/19/2025 Posts: 129 Rating:
|
hi are you use the CP1613 in the server how mutch the destance between server and client
|
2/3/2014 4:14 PM | |
Posts: 73 Rating:
|
Thanks for you reply, Iam using 2 CP1623 in each server, since my controller is H sytem. And the distance is approx 6mtrs. |
4/5/2014 9:06 PM | |
Joined: 9/27/2013 Last visit: 1/7/2025 Posts: 2 Rating:
|
Hi NoName, Yes, in my CPUs 417- 4H I updated firmware to actual V4.5.6 6ES7 417-4HT14-0AB0 Link to Operating SystemUpdate |
9/1/2022 3:04 AM | |
Joined: 2/22/2021 Last visit: 3/24/2024 Posts: 114 Rating:
|
How did you solve your problem? the same thing is happening to me. |
9/1/2022 5:21 AM | |
Joined: 9/9/2015 Last visit: 3/24/2025 Posts: 732 Rating:
|
Hi, Slow response might due to too many scripts execution or cyclic execution. To verify: 1. Go to C:\Program Files (x86) \Siemens\WinCC\uTools -> apdiag.exe 2. Output windows -> Open 3. Activate your wincc runtime, check script error "OnErrorExecute" 4. Check error page by page. Check also the dynamic tag execution, ensure tags set to "Upon Change Only" or "picture cycle " Change. If you use Standard cycle, then the execution will cause a slow down on HMI navigation. Ensure maximum 50 dynamic block icons on each screens. Too much block icons could cause slow response or the worst case can cause script ActionOverflow (More than 10000 Actions to work), then lead to Script EndAct eventually. Hope this is helpful. |
Please give me 5 stars Rating if my post is helpful for you. :) |
|