7/24/2015 8:40 AM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating: (1054) |
hi Allen, 1. yes you can. You can parametrize each channel-group for its own. you also have an own measure range module for each channel-group. 2. you don´t need the ext. compensation by 2-wire transducers, like you can see in the manual, chapter 6.7. Be sure that you really have a 2-wire-transducer. If it has an external power supply, you probably have a 4-wire-transducer. Therefore you should use the external compensation. Be sure that the compensation i grounded(functional ground). hope this helps, regards, |
FCK WAR! |
7/26/2015 7:58 AM | |
Posts: 36 Rating: (0) |
Hi mopS04. AttachmentWiring Diagram.pdf (272 Downloads) |
11/8/2017 10:22 AM | |
Joined: 6/19/2017 Last visit: 9/6/2024 Posts: 8175 Rating: (171) |
New question published by neO0O is split to a separate thread with the subject S7-300 redundant signal. Best regards |