4/30/2013 8:42 AM | |
Joined: 1/3/2006 Last visit: 2/19/2024 Posts: 726 Rating: (71) |
Hi SM335 has 8 channels, out of which 4 are input and 4 are output. Among 4 inputs 2 channels are fixed as Voltage inputs whereas remaing 2 channels can be configured as current or voltage. So you can connect your transducer to 3rd or 4th channel of AI card after configuring it as current (4-20mA) in hardware configuration. Attached file gives necessary information. And over herecomplete manual. Regards Manmeet
AttachmentSM335.pdf (71 Downloads) |
4/30/2013 8:48 AM | |
Joined: 1/21/2013 Last visit: 9/4/2024 Posts: 4620 Rating: (707) |
Hi Raffy, Have a look page 11,14.etc.. S7-300 SM 335 - Siemens Industry Online Support |
4/30/2013 9:23 AM | |
Posts: 209 Rating: (2) |
Ok now I get it..thanks guys... |
4/30/2013 11:08 AM | |
Joined: 1/3/2006 Last visit: 2/19/2024 Posts: 726 Rating: (71) |
Hi Raffy If one channel is voltage and other at current then module needs to be set at position 'A'. Refer to part of manual attached. Regards, Manmeet.
AttachmentSM335_A.pdf (52 Downloads) |