5/27/2008 10:04 PM | |
Joined: 4/3/2008 Last visit: 4/22/2024 Posts: 385 Rating: (16) |
Can you ping the pc? Is there any licence installed? pigroplc |
5/4/2010 10:15 AM | |
Posts: 17 Rating: (0) |
got the same problem! I will follow this thread for an sollution! |
8/4/2010 11:18 AM | |
Joined: 5/27/2008 Last visit: 2/29/2024 Posts: 29 Rating: (0) |
I've got to check if the firewall is active on my PC. |
12/8/2010 11:32 AM | |
Joined: 5/27/2008 Last visit: 2/29/2024 Posts: 29 Rating: (0) |
I'm setting up a second identical system (Panel PC 477), the ideal moment to test the malfunctionong things of the first system. What I found about taking remote control to a Panel PC via sm@rtservice: - Windows Firewall: Instead of disabling the windows firewall, just make sure that in the tab "Exceptions" the following exceptions are activated: - WinCC flexible RT module smartserver (program: \\path\smartserver.exe) - Webserver (HTTP) (port: 80 TCP) - Remote control: http://<IPaddress>:5800 works indeed, it activates the java applet and after entering the pwd, taking remote control of the panel PC is possible. => but I want to be able to start the "website" of my WinCC flexible application on the panel PC, like it is possible on a regulare panel by entering : http://<IPaddress> but then there appears a message "HTTP 500 - Internal server error Internet Explorer" Does somebody know what's missing? Has it to dosomething with IIS? |