10/10/2019 12:53 PM | |
Joined: 1/15/2019 Last visit: 10/27/2021 Posts: 16 Rating:
Hi guys, I am still rookie with SIMATIC PLC handling. My problem is the following one - I connected one AI module (SM1231 AI 8x13 bit) to my CPU and set the first 2 channels as current inputs (4-20 mA). The problem is that both my probes (first one for T, second one for H) are passive and therefore I got no current through the loops. Do I need to add an external power supply into each loop or there is workaround solution? I am enclosing some screenshots for providing more information. Thanks in advance for any advice. Regards, Primoz ------------------------------------------------------------------------------------------ AttachmentI-probes.zip (20 Downloads) |
Last edited by: The Helping Hand at: 10/10/2019 13:51:02New subject after splitting |
10/10/2019 4:34 PM | |
Joined: 7/7/2010 Last visit: 1/26/2023 Posts: 13078 Rating:
For your PLC input module, have you reviewed the reference wiring diagrams from the module manual? It shows how to wire up passive 4-20mA devices, from external power supply + output, through sensor, through plc input + and out plc input - to power supply's common (0V).
science guy |
10/21/2019 7:51 PM | |
Hi 0_Einstein, I did according to the manual and the scheme attached (see screenshot 4AI_Wiring). Can you please check whether I miss something (have a look at screenshots Wiring2PLC and Wiring2probe)? I select the 4th channel at module, the brown wire is the power supply (+24VDC), the blue wire is GND and the white one is the probe return. I also checked the voltage at probe`s terminals and it`s below 5 V, far to low I think. Is it possible that I ruined something at module? The TIA portal reads the input current signal as 32676 value (see the screenshots TIA - Screenshot#1 and TIA - Screenshot#2). Btw - with V-type channels (+/-10V) I don`t have any problems. Thanks in advance for any tip. Regards, banci AttachmentScreenshots.zip (36 Downloads) |