7/7/2011 10:41 AM | |
Joined: 3/24/2009 Last visit: 7/9/2024 Posts: 535 Rating: (112) |
Dear Ross, I'm quite sure, that the 6 bytes from the software are correct and the manual is wrong. Best regards, yy1 |
7/8/2011 3:21 PM | |
Joined: 10/7/2005 Last visit: 9/17/2024 Posts: 3020 Rating: (1054)
|
HelloRoss the latest manual I can find (Edition 01-2010) still has the 326-2BF01 in it which does occupy 8 Bytes of Output addresses (as did it predecessor the 326-2BF00). The 326-2BF10 however seems to occupy only 6 Bytes of Output addresses in the HWconfigwhich I suppose you will need to trust (or send a support request to Siemens for clarification and let us know the outcome). |
Cheers |
|