12/1/2011 4:20 AM | |
Joined: 11/21/2007 Last visit: 8/22/2023 Posts: 2321 Rating:
Hello The Module Specifications of SM331 specifies that the the ( M- ) connections of various Voltage / current signals should be connected together. ( Pl see attached Data Sheet ) Practically also I have seen that reliable and accurate measurement is only achieved when M- of analog signals is at the same level. Therefore I think that you need to modify the circuit so that all resistances are on L+ side only and M- is directly connected to the 0V. Also all 0V ( M- ) should be connected to each other. Hope this helps Cheers Navnag AttachmentS7300_AI_331_Module.pdf (97 Downloads) |
There is no such thing as the last bug in a program |
12/1/2011 7:30 AM | |
Posts: 4 Rating:
Thanks for your fast reply. Meaning, all the channels M- terminals will be connected to each other? |
12/2/2011 10:18 AM | |
Posts: 4 Rating:
Hi Navnag, Thank you very much, the issue has been settled. M- will be connected to the -V of the supply. Thanks alot for your ideas it helps me alot. |