12/29/2009 4:50 PM | |
Joined: 4/24/2006 Last visit: 9/29/2023 Posts: 8593 Rating:
Dear Tomy Master, Yes, it is possible. Here is link to manual: http://support.automation.siemens.com/WW/view/en/8859629 See chapter 6.6 In hardware configuration, you can specify the measuring range per Channel group. Then you must make the right wiring. Best regards, Wizard |
12/29/2009 5:00 PM | |
Joined: 4/19/2008 Last visit: 9/13/2023 Posts: 1525 Rating:
Hi Tomy, Yes you can configure the channel please have a look on Screen shot this module is having following Specification, ● 8 inputs in 8 channel groups ● Programmable resolution at each channel group (12 bits + sign) ● Programmable measurement type per channel group: –Voltage –Current –Resistance –Temperature ● Any measuring range per channel AttachmentAI.pdf (395 Downloads) |