10/3/2021 7:52 PM | |
Joined: 9/27/2006 Last visit: 2/14/2025 Posts: 12336 Rating:
|
Hello eng.mohamedaly; Let,s say the Moxa gateway is configured and parametrized properly for a Profibus DPV1 master (which is the only thing they mention in their manual): https://moxa.ru/files/manuals_nport/mgate_5101-pbm-mn_um_e5_0.pdf The Moxa gateway can only act as an interface between 2 different networks, by itself it cannot act as a Profibus DPV1 master. That means the BMS system must act as a Profibus DPV1 master and provide DPV1 commands and data record requests over the bus to a DPV1 slave. Is your BMS system capable of doing so? Which BMS system acts as master? What communication card is it using for Profibus DPV1? Do you have any documentation that describes how the master can request DPV1 quesries from the slaves on the bus? On the other hand: to act as a Profibus DPV1 slave, the Sirius softstarter must be a product version 04, you should verify what version your own module has. Version 03 cannot act as a DPV1 slave, as per this document: https://support.industry.siemens.com/cs/ww/en/view/35202974 Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 10/03/2021 19:54:40 |
|
10/3/2021 8:33 PM | |
Posts: 7 Rating:
|
Dear Daniel, thanks for your support, As per MOXA supporting team gateway support to read profibus DPV1 please check below photo. BMS system supporting BACnet and Modbus RTU and Modbus TCP only. communication Card 3RW4900-0KC00 E04 as below photo. [snip] thanks Attachmentimages.zip (827 Downloads) |
Last edited by: eng.mohamedaly90 at: 10/03/2021 20:55:27Last edited by: eng.mohamedaly90 at: 10/03/2021 21:01:22Last edited by: Jen_Moderator at: 10/04/2021 11:56:54Removed links and added files as an attachment. |
|
10/4/2021 6:51 PM | |
Posts: 7 Rating:
|
Hello, Anyone face the same issue before. |
10/5/2021 4:00 PM | |
Joined: 9/27/2006 Last visit: 2/14/2025 Posts: 12336 Rating:
|
Hello eng.mohamedaly; Compare this file to the one you are using now (you can open .gsd files with any text editor, such as Notepad). The link to this file is: https://support.industry.siemens.com/cs/ww/en/view/113630 You could have located this link easily, with the search box at the right of this page, using for example the search term GSD file for 3RW44. This search feature would serve you well in future inquiries. Try it... Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 10/05/2021 16:03:06 |
|
10/5/2021 6:31 PM | |
Posts: 7 Rating:
|
Hello Daniel, Thanks for your support, This is the same GSD file which i used but as per attached photo enable only 1 slot which converting the first 2 bytes, and there is no option to add more attached photo also for VFD which allow to add up to 20 slot so the limitation for GSD file not from the gateway, i tried to use GSD file for 3RW55 for testing but it is need authorization to download. [snip] please can you check from your side. AttachmentFiles.zip (949 Downloads) |
Last edited by: Jen_Moderator at: 10/06/2021 07:16:04Removed link and added files as an attachment. |
|