Posts: 21 Rating:
|
Hi HugoD, Have you found any solution to this problem? I get the same error. |
3/10/2017 3:04 PM | |
Posts: 439 Rating:
|
Hi Pavel,
Yes I have, sorry things are going so fast. I opened a support request with Siemens USA and here is what they told me.
So, I did remove the line "<group2>2</group2>" and it totally works. See attach zip file. Have a good day! Hugo AttachmentCapture.zip (85 Downloads) |
6/2/2017 1:31 PM | |
Joined: 4/11/2012 Last visit: 5/17/2024 Posts: 3 Rating:
|
Hi everyone, I had the same problem with an S612 and an SSC. After some tries and some injuries and thanks to Hugo I'll have the solution that is similar of the other one. In pratical the problem was related not even the String <Group2><Group2> but also in the first part the group number must be 2. In my case software put this value automatical to 14 and that get this error. See attachament also for further information AttachmentScreenShot Siemens.zip (91 Downloads) |