Hello Experts, We have three softstarters 3RW4436-6BC44 with communication module 3RW4900-0KC00 version E04. They are in same profibus line and two of them fails with bus fault. The line was checked and measured and seems okay. Same GSDs downloaded and i dont think problem is that. I just wonder if any critical point existing to communicate with these softstarters by DCS or different brand of PLC. Thank you for your support. ------------------------------------------------------------------------------------------ |
Last edited by: Min_Moderator at: 10/9/2015 3:01:40 PMNew subject after splitting |
|
10/18/2015 6:26 PM | |
Posts: 5 Rating:
|
Thank you for your support. Problem was solved with modified new model of communication board. Best regards |