Joined: 9/27/2006 Last visit: 9/15/2024 Posts: 12282 Rating: (2683) |
Hello vinu; Software redundancy does not require that CPUs be of same MLFB and revision. Actually you can use SWR on a S7-300 and a S7-400 together.These are the only hardware requirements: SIMATIC S7-300/S7-400 Software redundancy for SIMATIC S7 3.2 What hardware is required? Two S7-300 and/or S7-400 stations form the core of hardware requirements and are each equipped with a CPU and a connection for a DP master system. The two stations are linked by means of a bus system that you can use to exchange data. The I/O devices are interconnected by way of two DP master systems: One DP master system on station A and on one station B. ET 200M distributed I/O devices with redundant DP slave interface module IM 153-2 are connected to DP master systems. The DP slave interface module allows the failover from the first to the second interface in the event of a fault in order to forward process status data from the second DP master to the I/O. |