Hello patel, Short Answer: Using active bus is mandatory with redundancy. Detailed Answer: When you order the Redbundle, you recieve two IM153-2 and one bus unit IM/IM. Each IM should be mounted on the bus unit and conneceted to one CPU. So, the bus unit mission is not only handling hot-swapping function, but also connection to the active CPU. Moreover, Not all S7-300 CPUs support hot-swapping function. It's allowed only for high end S7-300 CPUs and S7-400 CPUs. Thus because, you will need to download OB83 (for Insert / remove). And this OB is not available for most S7-300 CPUs. For you case (CPU315-2DP), It does not support OB83. Hope this helps.
|