6/16/2009 9:35 AM | |
Posts: 6 Rating: (0) |
Hi Everyone, I have roblem with the software redundancy.I am trying to make redundancy between two 315 2DP CPU using MPI connection.I made hardware config and the block parameters according to the SWR Manual.However, when I try to run both CPUs, one of them always stops and creates a system fault.I checked my blocks and my FB101 block creates "W#16#8015Redundant-backup link failure."error code..I am sending my program attached.Could you please check and tell me what I am do wrong? Thank you from now, Burak, AttachmentSWR_S7-300.zip (381 Downloads) |
6/16/2009 12:31 PM | |
No answer so far... Isn't there nobody who use mpi for software redundancy??Please help me I have to solve this problem today.. |
6/16/2009 1:58 PM | |
Hi H-H, Thank you very much for your response, I did exactly what you said.But the same problem stillexists.When one PLC runs,other one stops with a system fault. |
6/17/2009 7:21 PM | |
Joined: 7/2/2008 Last visit: 8/26/2024 Posts: 928 Rating: (308) |
Hello Burak, First, thank you very much for your feedback. Second, I'm quite happy as you could find out where the problem is. Well, I can't find anything in manualsaying thatMB length must not equal 1 or any other odd number. Anyhow, the problem is solved and another restrictionwill be considered in the future. One little thing, I had a smallproblem to open your project since it wasn't language neutral. Try to make your uploaded project Language neutral (If possible) to allow more people to open your project quickly. http://support.automation.siemens.com/WW/view/en/22635865 Best regards. H-H |