1/7/2013 11:36 PM | |
Joined: 10/7/2005 Last visit: 9/18/2024 Posts: 3021 Rating: (1054)
|
Hello ROHIT PHUTELA I'm afraid to say that this isstillNOT possible (to be precise, it would be possible, but Siemens has not yet developed a Software redundancy package that contains the required comms Blocks to alllow usage of the PN port for the redundancy link). While you can use PN CPU's in general for a Software redundant system, you can only link the two via MPI, or external CP (Profibus or Ethernet). The Which modules can you use when implementing software redundancy? link contains a section for supported CP's and more info is also available in the manual (also available via the above link). I hope this helps |
Cheers |
|
This contribution was helpful to1 thankful Users |
4/20/2013 7:23 AM | |
Posts: 319 Rating: (9) |
Thanks for the info |
3/12/2014 8:30 AM | |
Posts: 340 Rating: (6) |
new question is splittet to S7 315-2PN/DP, which interfaces has PLC, connect to SCADA |
4/7/2014 4:32 AM | |
Joined: 10/7/2005 Last visit: 9/18/2024 Posts: 3021 Rating: (1054)
|
Hello Shreyas I'm afraid to say that the answer is still the same as my previosu answer above and as followed (just in case this thread gets split):
|
Cheers |
|
This contribution was helpful to1 thankful Users |
5/16/2016 7:27 AM | |
Posts: 1 Rating: (0) |
Has there been any update on using the PN port for redundancy instead of the MPI? |