Hello, which order-no? 6ES5 095-8M___? Regards André Räppel --------------------------------------------------------------------------------- www.raeppel.de
work faster withinnovative PLC-Tools |
5/9/2014 9:18 AM | |
Posts: 4 Rating: (0) |
Hi the S5-95U order no. 6ES5 095-8MB02, commucation port: SINEC L2. thanks! Best regards Bruce |
5/9/2014 9:23 AM | |
Joined: 4/5/2006 Last visit: 8/13/2023 Posts: 642 Rating: (131) |
Hello, i would use a 6ES5 8ME__ and connect it via DP-DP-coupler. 8MB02 is L2, not DP. How much data for communication? Regards André Räppel --------------------------------------------------------------------------------- www.raeppel.de
work faster withinnovative PLC-Tools |
5/9/2014 9:48 AM | |
Joined: 10/7/2005 Last visit: 10/4/2024 Posts: 3024 Rating: (1054)
|
Hello Bruce0919 your S5-95U (6ES5 095-8MB02) supports FDL protocol which allows you to link it to an S7. What you need is a CP342-5 in the S7 and you'll find configuration examples at Where can you find sample programs and documentation for communication from SIMATIC S5 modules to SIMATIC S7 modules by way of PROFIBUS using the FDL protocol? I suggest you also grab a copy of the SINEC L2 Interface of the S5-95U Programmable Controller as a reference. I hope this helps |
Cheers |
|
This contribution was helpful to1 thankful Users |
5/9/2014 10:56 AM | |
Joined: 4/5/2006 Last visit: 8/13/2023 Posts: 642 Rating: (131) |
Hello, which Panel? TP15? Or you mean OP15? Regards André Räppel --------------------------------------------------------------------------------- www.raeppel.de
work faster withinnovative PLC-Tools |
5/12/2014 11:30 AM | |
Joined: 10/7/2005 Last visit: 10/4/2024 Posts: 3024 Rating: (1054)
|
Hello Bruce0919
not too sure if I understand this correctly. You would already have SINEC L2 cable in place wouldn't you? If so, it may not look like new (purple) Profibus DP cable, but you'll find that it will most likely do the job (certainly at lower baud rates). Question is: What type of cable is currently installed?
No problems, as said before, your S5-95U (6ES5 095-8MB02) support FDL protocol which allows you to link themto an S7.
CP340 is for all sorts of serial comms, butdoes NOT support the "Profibus" protocols that the onboard interface of your S5-95U (6ES5 095-8MB02) supports. --> Go for the CP342-5 instead. I hope this helps |