3/6/2020 2:06 AM | |
Posts: 29 Rating:
|
Can't figure now how I should do this.. 2 problems present. Attached the LSC, and that will also have explanations of things on it. 1. Having some problem with things starting to happen at power on, before user pressing START. 2. Pressing STOP does not put everything to halt if the timers happen to be running.. STOP button only works in case the Q1 or Q2 would at the moment be ON.. Thanks for your help Attachmentproblem.zip (98 Downloads) |
Last edited by: tenuke at: 03/06/2020 02:06:49Last edited by: tenuke at: 03/06/2020 09:28:49Last edited by: tenuke at: 03/06/2020 09:29:02 |
|
3/6/2020 4:46 AM | |
Joined: 12/18/2014 Last visit: 12/6/2023 Posts: 31561 Rating:
|
Solution like this?
AttachmentOut_in_FS4.zip (82 Downloads) |
3/6/2020 8:56 AM | |
Joined: 9/11/2014 Last visit: 12/6/2023 Posts: 679 Rating:
|
Hi, in LSC you can compare LOGO! programms. Open both version in LSC and then select Tool/Compare. Hope this helps |