8/6/2020 2:13 PM | |
Joined: 10/11/2006 Last visit: 10/11/2024 Posts: 5911 Rating: (809)
|
Hello, max. speed is limited in drive P1082. There is an Reference value for 100% in P2000. This reference value in P2000 must fit to the reference value at the TO, because correct data transfer. It makes no sense to set Limitation at TO > P1082. Reference value *2 = Max speed = 200% There is an example: Configuring Technology Objects with SIMATIC S7 1500 and SINAMICS S210 in TIA-Portal https://support.industry.siemens.com/cs/de/en/view/109749795 There is an example for an control block: LaxisCtrl https://support.industry.siemens.com/cs/de/en/view/109749348 |
With best regards, |
|
8/6/2020 8:35 PM | |
Joined: 5/22/2012 Last visit: 3/24/2022 Posts: 895 Rating: (67) |
You see that the velocity unit is mm/s and not rpm? |
8/10/2020 9:58 AM | |
Joined: 12/12/2013 Last visit: 12/15/2023 Posts: 7 Rating: (1) |
|
8/10/2020 10:19 AM | |
Joined: 12/12/2013 Last visit: 12/15/2023 Posts: 7 Rating: (1) |
|
8/10/2020 10:51 AM | |
Joined: 12/12/2013 Last visit: 12/15/2023 Posts: 7 Rating: (1) |
|
Last edited by: DavidJermol at: 08/10/2020 10:54:08 |
|