Thanks for your help. My motor is 1FK7103-5AF71-1FH0 You mean that lower than Mmax value, upper than Mstall, it can run in intermittent way.
|
9/28/2012 6:56 PM | |
Posts: 767 Rating: (69) |
Hello kelese, Yes,lower than Mmax value, upper than Mstall, it can run in intermittent way. Attached is torque vs. speed curve for the motor. 1FK7103-5AF71-1FH0. On these curves a reference is made to S3 curves, which are for intermittent duty. For instance, S3-25% means that the motor has capability to support torque vs. speed along this curve 25% of time for a duty cycle of 10 minutes where the starting current has little effect on temperature rise. During remainder 75% of time for duty cycle of 10 minutesthe motor is not producing any torque or speed; therefore, the motor cools during this time period. Best Regards, Deputy AttachmentC:\Documents and Settings\summrl\My Documents\FY12\Reference\Forum\1FK71035AF Torque Curve.jpg (654 Downloads) |
1/7/2014 12:23 AM | |
Joined: 9/1/2005 Last visit: 12/12/2024 Posts: 4114 Rating: (195) |
follow up question published by apolobris split to a seperate thread with the subject trying to get the graph torque vs. speed Best regards |