11/6/2020 5:28 AM | |
Joined: 5/27/2020 Last visit: 6/21/2023 Posts: 28 Rating: (0) |
Hi Guys, I am using G120 drive CU240E 2F standalone without PLC for a winder application. I have programmed the drive in Torque control mode and it runs well. But i know there is a potential runway situation if the cable breaks. So i thought of making use of free FFB in the drive to program it in such a way that it switches to speed control if actual torque is less than 12Nm. But i am unable to use the actual torque feedback in FFBs. Is there any other parameter which can suffice this. r31 is the parameter which shows actual torque feedback but its not showing when i tried to link with a NCM input. Can any one help me out with a solution. Or is there any other way?... Regards VJ Attachment2020-11-06 15_26_56-STARTER - Dispatch Winder - [G120_CU240E_2_F.Control_Unit - Expert list].png (127 Downloads) |
11/6/2020 2:23 PM | |
Joined: 10/11/2006 Last visit: 4/18/2024 Posts: 5819 Rating: (787)
|
Hello, This is explained in the following application example. https://support.industry.siemens.com/cs/ww/en/view/60602336 |
With best regards, |
|
This contribution was helpful to1 thankful Users |