Posts: 102 Rating:
|
Hi PicLaci You could do it like this: bundle your inputs/outputs in bytes in the tag table (be careful to only read them, else you might cause massive problems!) in the example's case, I wrote them to a DB's variables. (to be sure they can't be written directly from the HMI - not really neccessary, but a small precaution) Then hand them over to the HMI in the HMI tag-table. Insert an "I/O-Area" - Element to your HMI-page, set it to "Output" and assign the variable. Set the dataformat to binary, set it to show 8 elements and transfer it to your PLC and HMI. AGAIN: Take precautions not to write these InBytes or OutBytes by accident, because you might overwrite an In- or Output and cause potentionally dangerous problems with your machine!! Aside from that, it's a nice addon to be able to see the active INs and OUTs, thanks for the idea! EDIT: When I look at my post, I can't see the images, if that's a problem with my PC or if they are not loaded, I can't say... They show up when using the "Quote" function though Attachmentpictures.zip (81 Downloads) |