11/12/2020 7:01 PM | |
Posts: 7 Rating: (1) |
Hello, I am pretty much entirely new to Siemens PLCs and one of our production machines had an issue lately. Machine started acting funny and finally stopped working at all. One solid red LED (SF) and one blinking red LED (BF) on the S7-300 PLC. I checked inside the diagnostic buffer and have attached that to this post. Having a hard time figuring out what all this text means. I think it has something to do with a slave station 9 (have only a mild idea of what a slave station is). Does anyone have any idea how I could trace that back to a physical device? Please note the PLC is in STOP mode. Thanks, Maintenance Jeff Attachment501_2_red_leds.txt (230 Downloads) |
11/13/2020 1:20 AM | |
Joined: 9/27/2006 Last visit: 6/4/2024 Posts: 12260 Rating: (2670)
|
Hello Jeff; This manual page for the ET 200PRO distributed I/O station, headed by a IM154-1 DP module, shows how the Profibus address is configured on that module: https://support.industry.siemens.com/cs/ww/en/view/21210852/35612389003 Since BF indicates a Bus Fault, it would be worth looking at the address that is setup on the IM 154-1 DP, and compare it to the the Profibus configuration (in HWConfig) and the diagnostic buffer entries that reference OB 86 (I/O rack fault). Also tell us if the IM 154-1 is one of the end-nodes on your network, in which case the terminator circuit shown in the link above should be set active; if not, it must be deactivated. Hope this helps, |
This contribution was helpful to2 thankful Users |
11/13/2020 4:38 PM | |
Posts: 7 Rating: (1) |
OB86 is already in the PLC, that message was from when the PLC was in STOP. I have attached a new diagnostic buffer after startup in RUN mode. I think I am confusing IM 154-1 and station 8 due to their close physical proximity on the machine. Sorry about that. As for the DP addresses there are small physical switches on the interface of station 9 and station 8 that indicate what their DP slave number/station number is. I believe these switches need to match up with the programming. Looking at the diagnostic buffer now in RUN mode, I do not see any issues at all with the PLC, but please double check me. I think the next step is to find where communication fails in the Profinet with HW Config tool. Again, I have confused IM 154-1 with station 8. I believe the failure is at IM 154-1 based on HW Config tool and I will investigate that device physically further. Thanks, Maintenance Jeff Attachment501_cpu_msg.txt (197 Downloads) |
Last edited by: Maintenance Jeff at: 11/13/2020 16:39:37 |
|
This contribution was helpful to1 thankful Users |