3/18/2019 5:53 AM | |
Joined: 1/1/2017 Last visit: 2/21/2025 Posts: 337 Rating:
|
Hello All, The problem is that I've communicated with the Third party device & ping operation is taking place as it is. But the Status node in TSEND block is showing F#7000 value which means that TSEND lock is neither receive any value from the Third party device not sending that to it. Hence how to sort out this issue please guide me. Regards OmKris ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 3/18/2019 8:10:09 AMNew subject after splitting |
|
3/18/2019 8:40 AM | |
Joined: 7/9/2015 Last visit: 3/14/2025 Posts: 4198 Rating:
|
Hi, when REQ will be true, please check Error / Status like described in the following FAQ: How do you evaluate the status of system blocks in STEP 7 (TIA Portal)?Regards, Towome |
|
|
3/18/2019 1:48 PM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating:
|
hi OmKris, did you establish a connection with TCON? Have a look to the application sample: Basic Examples for Open User Communication (OUC) hope this helps, regards, |
FCK WAR! |
|
This contribution was helpful to
1 thankful Users |
3/21/2019 10:37 AM | |
Joined: 1/1/2017 Last visit: 2/21/2025 Posts: 337 Rating:
|
Hello MOP, Thanks for your help. I've successfully created the communication via the TCON & TSEND block. [snip] Regards OmKris AttachmentSample_V14_20032019.zip (195 Downloads) |
Last edited by: Jen_Moderator at: 3/22/2019 8:58:51 AMDivision of questions into seperate topics. |
|