7/25/2007 3:21 PM | |
Posts: 37 Rating: (0) |
what mean by exclusion address & termination address in Step 7 V5.4 SP1 FB varaible. for what purpose they are used. |
11/14/2015 3:25 PM | |
Posts: 1 Rating: (0) |
pushing it up ..
|
11/14/2015 6:28 PM | |
Joined: 9/27/2006 Last visit: 9/18/2024 Posts: 12282 Rating: (2684)
|
Hello guys; Just in case the subject is still pertinent, "Exclusion addresses" and "Termination addresses" are parameters attached to a runtime diagnostic package named PDiag, for Step 7: See the following extracts:
S7-PDIAG for S7-300 and S7-400 Configuring Process Diagnostic
https://support.industry.siemens.com/cs/ww/en/view/16531809
7.8 Defining Termination Addresses
The use of auxiliary networks for criteria analysis will be aborted immediately when a termination address is reached.
You can select one of the following methods of defining termination addresses, depending on whether you are going to select this address in S7-PDIAG or in the LAD/STL/FBD editor.
7.9 Defining Exclusion Addresses
You can define Exclusion Addresses.
The criteria analysis function hides those addresses and auxiliary networks you are working on if they have been assigned a "0" value (only in conjunction with ProAgent, Version 5.0 or higher).
You can choose one of two methods of defining exclusion addresses, depending on whether you are going to select this address in S7-PDIAG or in the LAD/STL/FBD editor.
Hope this helps, Daniel Chartier |
This contribution was helpful to3 thankful Users |