6/18/2016 12:07 PM |
|
Posts: 92 Rating: (5) |
hello there 5010\5012 : 00000100 5011\5013 : 11000111 cable is tested with Diode & still work with "PCIN" ------------------------------------------------------------------------------------------ |
Last edited by: Min_Moderator at: 6/20/2016 1:30:05 PMNew subject after splitting |
|
6/27/2016 10:12 AM | |
Joined: 1/30/2007 Last visit: 6/3/2022 Posts: 262 Rating: (24)
|
Hi Sky Diver840, the cable you are using to connect pcin won't work in connection to the plc 'cause pcin uses rs232 interface whilst the plc demands a current loop 20 mA interface. This current loop interface is not provided by a pc or laptop but only by a pg. Using a pg 7xx (or field pg or power pg) you ought to have a cable 6ES5734-2xxxx to connect to a S5 plc. As I recall the Sinumerik 810 is connected to a plc S5-150 hence you 'll need an adapter described in this link: https://support.industry.siemens.com/tf/de/en/posts/54093 If you are working on a pc the pc-plc-adapter cable of Siemens won't work because it needs a 5V supply provided by the plc in the pg interface. I'm sorry but the pg interface in the S5-150 doesn't provide this 5V supply. To solve this topic I recommend to use this usb - S5-adapter provided by cd-elektonik: http://www.cdelektronic.de/products/S5_PG-USB/s5_pg-usb.html You 'll need these items to connect to a plc 150: Good luck |
This contribution was helpful to1 thankful Users |
9/19/2016 7:10 AM | |
Posts: 92 Rating: (5) |
Thanks dear sr I set the MD , but there was some noise on my connection system , anyway I make it solve best regards russell |