6/11/2011 5:13 PM | |
Joined: 10/7/2005 Last visit: 12/12/2024 Posts: 3029 Rating: (1057)
|
Hello Vasya I suspect "Type check of addresses" is ticked and causes the problem (assumption: variable "#di_refpos" is of type DINT in which case the LAD/FBD type check of addresses "complains" about the "OD" instruction which expects DWORD data types and will lead to the network being displayed in STL). To fix it, open any block, go to the Options menu, select Customize and untick "Type check of addresses" in the LAD/FBD tab. I hope this helps |
Cheers |
|
This contribution was helpful to2 thankful Users |
6/12/2011 1:19 PM | |
Posts: 19 Rating: (1) |
IT WORKS!!! Thank you very much! |
This contribution was helpful to2 thankful Users |