9/14/2020 11:51 PM | |
Joined: 3/3/2020 Last visit: 11/11/2022 Posts: 43 Rating:
|
The stepper motor is naturally pulsed. |
9/17/2020 8:13 PM | |
Joined: 12/18/2014 Last visit: 12/5/2023 Posts: 31546 Rating:
|
I don't think that the transistor outputs of the LOGO! can switching with a frequenz of 3 kHz. |
9/17/2020 8:32 PM | |
Joined: 12/18/2014 Last visit: 12/5/2023 Posts: 31546 Rating:
|
Siemens does not provide any precise information. According to the manual it is 10 Hz. But there is an addition that the maximum switching frequency depends on the current cycle time. And the cycle time in turn depends on the type and size of the LOGO program. Therefore Siemens cannot give precise details.
AttachmentLOGO! 8 manual 0BA8 2017_11 xxxx8-0BA0.pdf (82 Downloads) |
This contribution was helpful to
1 thankful Users |
9/17/2020 8:54 PM | |
Joined: 12/18/2014 Last visit: 12/5/2023 Posts: 31546 Rating:
|
May be I understand you not correct. Want you only convert the 4-20 mA signal as 0-3 kHz for monitoring and displaying? AttachmentExample_0BA8.Standard.zip (77 Downloads) |