4/25/2009 12:09 PM | |
Posts: 10 Rating: (0) |
Hi guys, I need to connect4 stepper motor with s7-200 plc CPU 224 orneed to go for extra module.pls give me a solution for this communication. |
4/26/2009 6:42 AM | |
Joined: 9/27/2006 Last visit: 4/24/2024 Posts: 12257 Rating: (2665) |
Hello sarwan; For each stepper motor you will require a EM253 positionning module and a stepper power module. The EM253 is well described in the S7-200 System manual, with examples on how to connect it to different power modules from Siemens and other manufacturers. Here is an application note including code and calculation tables for acceleration, showing how to control a stepper motor with the EM253 and a FM Stepdrive power module: http://support.automation.siemens.com/WW/view/en/21061963 Hope this helps, Daniel Chartier |
4/26/2009 8:29 AM | |
Joined: 5/28/2008 Last visit: 4/15/2024 Posts: 4505 Rating: (835) |
Hello sarwen, Also you can use The CPU224 it self to drive two stepper motors using integrated two High speed Outputs "Q0.0 & Q0.1" Here's attched the high speed output instructions. The remaining stepper motors can be drived via EM 253. With best Regards, AttachmentPulse Output Instructions.pdf (585 Downloads) |
Ayman Elotaify |
|
This contribution was helpful to2 thankful Users |
4/28/2009 11:39 AM | |
Posts: 10 Rating: (0) |
|
This contribution was helpful to1 thankful Users |