Hello, basically you can use the OFF3 signal for quick stop and OFF1 for normal ramping down. There is an application example available which shows the use of speed changeover and quick stop via sensors. https://support.industry.siemens.com/cs/ww/en/view/58399364 Please keep in mind the fact that you have a delay when processing the sensors in the PLC. |