Hi there, Here I copy and paste what is manual said: OB 25: Addressing Error (ADF) An addressing error occurs when a STEP 5 operation references a process image input or output to which no I/O module was assigned at the time of the last COLD RESTART (the module is not plugged in, it is defective, or it is not defined in data block DB 1 of the CPU. The STEP 5 operation at which the addressing error occurred is processed completely: For bit operations, the bit in the process image is scanned and combined logically or set/reset. Load and transfer operations are also executed. Continued processing can, however, result in incorrect or unwanted reactions.
resumed at the next operation. If OB 25 is not loaded, the CPU changes to the STOP mode with an addressing error. The STEP 5 IAE operation disables addressing error monitoring for individual program parts or for the entire program. You can enable it again using the RAE operation (see Section 3.5.4 and List of Operations). |