hello, thanks for reply. i am attaching here a link of a manual of relay. --Deleted Link-- need help. thanks again. Attachment7SR11 and 7SR12 Argus Catalogue Sheet.pdf (613 Downloads) |
Last edited by: Jen_Moderator at: 11/17/2017 7:13:50 AMAdded PDF as an attachment. |
|
11/20/2017 4:08 PM | |
Posts: 3093 Rating:
|
Hello Chintu, Modbus RTU for CP341 uses the addresses of the data link layer as defined in the Modbus specification. So you must subtract 1 / 10001 / 30001 / 40001 from the ARGUS list. When you use input register 0 length 0F you read half of a double word. I think this is causing the error. So use address 0 and length 0E of 10. Regards, |
This contribution was helpful to
2 thankful Users |
11/22/2017 12:56 PM | |
Joined: 4/29/2016 Last visit: 3/15/2025 Posts: 31 Rating:
|
Hello sir, Still have an error of exception code 02. "Subtract 1/10001/30001/40001 from argus list," It means I am trying to read one data having address 30010, so I have to enter 0009 ?? Am I right?? Thanks |
11/22/2017 1:54 PM | |
Posts: 3093 Rating:
|
yes |