Hello Trong; I have extracted the procedure to change the Profibus address of the Sentron WL trip unit from the following communication manual: http://support.automation.siemens.com/WW/view/en/12560390 See the attached document. Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 11/26/2008 2:16 PMProblem with the attachment: text missing |
|