Hello 7gallon you are not missing anything, the "problem" is that open communications via T-Blocks are NOT supported via a CP343-1 (see also What differences are there between the Industrial Ethernet CPs of SIMATIC S7-300? on what connections are possible). If you want to use the CP343-1 for the comms you willneed toconfigure the connection the good old fashion way inNetpro. I hope this helps |