Hello kapil; Yes, you can instal a CP 343-1 on any of the 3 expansion racks supported by a IM 361. And standard functions AG-Send and AG-Recv are the ones you will use to transfer blocks with the CP. As far as the CPU connecting wth the correct CP, have a look at the following FAQ (it also contains a sample program that you can use as a base for your own blocks): http://support.automation.siemens.com/WW/view/en/17853532 Pay special attention to the parameters ID and LADDR, this is how NetPro and Step 7 ensure that you are using the right CP and the right connection. These parameter values are generated when you use NetPro to establish a connection, and are used as input parameters to AG-Send and AG-Recv. See the sample program for more details. Hope this helps, Daniel Chartier |