9/8/2011 11:47 AM | |
Posts: 40 Rating: (1) |
In sinamics I have newer version than i can select. I can select version 2.4, 2.5 or 2.6.1, but in sinamics is version 2603500. Do I need to update my step 7 device list or maybe downgrade CU FW to version 2.6.1? I did increase cycle times and allow 5 overflows now. Settings I used to have were found here:https://support.automation.siemens.com/WW/llisapi.dll?query=31xt_gs_sinamics_s120_en-US_en-US&func=cslib.cssearch&content=adsearch/adsearch.aspx&lang=en&siteid=cseus&objaction=cssearch&searchinprim=&nodeid99= I attach a picture of errors that appeared after I change cycle settings. BR, Taubek
|
Last edited by: taubek at: 9/8/2011 11:57 AM |
|
9/8/2011 1:32 PM | |
Joined: 8/31/2005 Last visit: 8/20/2024 Posts: 2198 Rating: (328)
|
I'm, not shure what version 2603500 is. If you enter the CF Card of the SINAMICS in a universal card reader, you can find the FW version in the file "content.txt" (or printed on the label of the CFcard, but there it may be out-dated) You should update to a supported version (or downgrade) But more importent is the next point:
|
|
|
9/9/2011 1:11 PM | |
Joined: 8/31/2005 Last visit: 8/20/2024 Posts: 2198 Rating: (328)
|
Yes, you must change the CPU in HW Config. There you select which version of the Technology Firmware is used. The problem is the MC_Power V3.0 does not work with the Technoclogy Firmware 3.1. And As long you did not change the T-CPU type in HW Config or use the MC_Power in V2.0 it will not run. I made a projext with a virtual axis. Please download it. It should run. With the variable table VAT_1 you can enable the axis and make and monitor a relative positionings. I will change it to your configuration and upload it too. AttachmentT-cpu_v411.zip (479 Downloads) |
Last edited by: miami at: 9/9/2011 1:13 PM |
|