2/8/2019 5:15 PM | |
Joined: 10/22/2018 Last visit: 5/27/2023 Posts: 5 Rating: (1) |
Hoping to get an answer here. When I add telegram 750 I get a link to parameters 1522 and 1523 positive and negative torque limits. This then generates an error as soon as I enable the drive stating that the limit is zero. I tried to write directly to those memory areas, but they get overwritten somewhere else. Also unable to deselect them from the telegram. Using Tia 14, starter 5.1. anyone have good suggestions? Thanks, Lars
------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 2/11/2019 10:26:24 AMNew subject after splitting |
|
2/11/2019 4:03 PM | |
Joined: 10/11/2006 Last visit: 12/5/2024 Posts: 5960 Rating: (820)
|
Hello, please use TO to handle the Telegramm 750. 5.4.2.3 Configuration - Data exchange with the drive https://support.industry.siemens.com/cs/ww/en/view/109749262 Supplementary data Select the "Torque data" check box if you want to configure the data connection of the torque data. If you have selected a drive with which the supplemental telegram 750 has been configured, the "Torque data" check box is preselected. 10.12.3 MC_TorqueRange V4 |
With best regards, |
|