Hello Buttsy39, first of all welcome to the forum. First: There is no "ABA0". And you won't have an 0BA0 either, it would be over 20 years old. It also cannot process analog values and no expansion modules can be flange-mounted. So you will have a LOGO! 8.2 whose article number ends with 08-0BA0, i.e. 6ED1 052-XXX08-0BA0. You can use all analog expansion modules with article numbers ending with 0BA2 on this. The threshold trigger is sufficient to switch a heater on and off. To do this, the switch-off value must be entered in the "ON" parameter and the switch-on value in the "OFF" parameter and then the output must be negated. An example in the attachment. The values for switching on and off can be changed via the display.