Hello,
FC105 is for S7 CPU not for S5.
to understand analog input conversion you have to read pag 9-24 of S5-135 system manual. With standard pt100 range (pag.9-26) 1 unit is 0,26°C. If you have 4-20mA temperature transducer input range is 2560-512=2048 unit (pag.9-28). Attached screenshot of my old s5 conversion block. Difference between scale limits is divedeb by 2048. Result (value for 1 unit) is multiplied by input units. Instruction SLW-SRW is to get rid of aux bits (sign-overflow-error). If something is not clear please ask again. Best Regards |
★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★ |
|
This contribution was helpful to1 thankful Users |
12/26/2017 10:02 PM | |
Joined: 7/2/2016 Last visit: 6/18/2024 Posts: 120 Rating: (29) |
Runaway7, mindware, I'm sorry I had not seen that I was at the S5 conference. |
hope this help, if it was helpful please rate the post! |
|
This contribution was helpful to1 thankful Users |
12/31/2017 2:26 PM | |
Posts: 80 Rating: (0) |
yeah.thank you. its done |