Hi Warnstromkraft, I do not know what workarounds you have already considered. However, I would recommend using the @ConnectionName_PLC_OpState system tag. Simply use this tag to trigger a script, get the tag value, and then access the quality code. This will give you the reported state of the PLC as well as the quality code, which will give you information about the state of the connection. Kind regards |