1/14/2025 9:33 AM | |
Joined: 8/3/2009 Last visit: 2/6/2025 Posts: 14656 Rating:
|
Hello Pieter1968 Please check out this FAQ: https://support.industry.siemens.com/cs/de/en/view/109759021 Bye Murof |
If this Information really helps, you could use the Rate function |
|
1/14/2025 12:52 PM | |
Joined: 1/30/2013 Last visit: 1/17/2025 Posts: 22 Rating:
|
Hi Murof, Thanks for your reply. I am aware of the multiligual settings as pointed out by you. The alarm text is working as intended and correct. I do get the alarm text in all activated languages. The alarm text is stored in the alarm log file (.csv format) but the info text is not. The info text is not loaded from the CPU into the Alarm view at the HMI unless I use the display option "Current alarm States" or "Alarm buffer" instead of "alarm log" or when the option "Automatic update" is turned off. So with the Display option set as "Current alarm States" or "Alarm buffer" everything,including the info text is working as intended and correct. Also with the option "Automatic update" turned off everything, including the info text is working as intended and correct. I do want the option "Automatic update" switched on and I do want to use a log file. Regards, |